SNVT_flow will not display correctly in Imperial units on a TGML graphic on a Xenta Server
  • SNVT_flow will not display correctly in Imperial units on a TGML graphic on a Xenta Server
‎2018-09-07 01:47 AM
Last Updated: Crewman ContentModerator ‎2025-10-10 02:55 AM
TAC Vista
  • Xenta Servers version 5.1.1 or earlier
  • Xenta 511, 527, 711, 731
SNVT_flow will only display on TGML graphics as liters per second regardless of what unit the signal in Xbuilder is configured for when sent to the graphic page. This is a bug and has been reported.
This has been corrected in version 5.1.2. Upgrading to 5.1.2 or later will resolve this issue.
If upgrading is not an option, the conversion can be done in a script element of the TGML graphic page. This LS to CFM Snippet can be used to modify a numeric or text presentation object.
ls to CFM Conversion.zip
  • 3222