How calculate the accuracy?
SHD100:
006902320
006902321
SHD100-T:
006902330
006902331
In the documentation, both "Accuracy" and "Temperature Dependence" is listed. The Temperature Dependence is varying (see data sheet for chart), while the Accuracy is constant across the scale.
The Accuracy and Temperature Dependence needs to be added together in order to calculate the correct total accuracy/deviation.