Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

SCU dip switch 6 for dual station addressing

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • SCU dip switch 6 for dual station addressing
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3580 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

SCU dip switch 6 for dual station addressing

Picard Product_Support
‎2018-09-10 03:42 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:57 AM

Issue

Clarification on dip switch six and station addressing for the SCU1200, SCU1280, or SCU1284

Product Line

TAC INET

Environment

  • I/NET Seven with Access Control using an SCU
  • SCU1200, SCU1280, or SCU1284

Cause

Clarification on SCU and dip switch settings being open, enabled for dual or single station addressing (2 or 4 doors)

Resolution

If the Device Type is SCU1200, SCU1280, or SCU1284:

  • set the Number of points to either 1 or 2.
    • Choose 1 if the SCU is configured to operate in the “single-address” mode (DIP switch S1-6 = OFF).
    • Choose 2 if the SCU is configured to operate in the “double-address” mode (DIP switch S1-6 = ON).

In order to control more than two doors, the SCU1284 must be configured to operate in the double-address mode. Though the TCON312 shows the dip switches for 1-6, there is still a bit of clarity which can be provided on how that looks on an actual SCU. The example from the TCON is shown here:

And this is a photo below of an SCU which is setup as 0101 with dual addressing since Dip Switch 6 is in Dual Address mode shown in the picture below. When penetrating down to it using Edit, Host Computer, Network Configuration, SCU 1284 is shown with 2 Points with door addresses:

  • 010108 Door1
  • 010109 Door2
  • 010208 Door3
  • 010209 Door4

After checking MCU Configuration, I added the points in the Network configuration. The main point here is that Dip Switch 6 is up on the Open side of the Switch bar shown in red which is the dual point and 4 door configuration.

 

Note: Concerning the numbering scheme for addressing the SCU, it is important to number your SCUs with an address then skip the next number so in the event you dual addressing for four doors, the second address is available. Don't use addresses 28, 29,30, and 31 as those are reserved for the Remote Arming Terminal.  Overlooking this can result in future headaches of moving SCUs around in the addressing scheme which is never recommended.

Example for a site containing 4 SCU door controllers: SCUa address 2, SCUb Address 4, SCUc Address 6, SCUd Address 8. 

Another example configuration: One reader inputs to READER1 and READER2? Here is that wiring example.

In order to use more than the first eight inputs on the SCU, you must configure the SCU as a double-address controller. When you enable the double-address mode (DIP switch S1-6 = ON), inputs 1 through 8 are monitored on the selected subLAN address (i.e., the primary address) and inputs 9 through 12 are monitored on the next consecutive subLAN address (i.e., the secondary address). The input points are defined in the I/NET host using two separate SCU controller assignments, the first providing eight input point definitions and the second providing 4 input point definitions.

The SCU’s outputs are also divided across two LAN addresses when the SCU is operating in the double-address mode. The first four outputs are assigned to bit offsets 00 through 03 on the SCU’s primary address. The last four outputs are assigned to bit offsets 00 through 03 on the SCU’s secondary address.

Labels (1)
Labels:
  • TAC INET
Attachments
Tags (4)
  • Find more articles tagged with:
  • 6318
  • additional
  • dpu
  • pinout
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore