Resolving I/O module device address changed and Blacklisted device detection errors.
  • Resolving I/O module device address changed and Blacklisted device detection errors.
‎2018-09-11 12:02 PM
Last Updated: Crewman ContentModerator ‎2025-09-01 03:36 AM
Some IO modules status showing as 'Blacklisted device detected" or "Address shift detected" or a system alarm is received indicating the condition.
AS trace logs may show one of the following entries...
2015-08-18 17:41:02.675 [1256862784] nsp.pin.cio.IODevice Module at address 14 is reporting Internal Error Code 32
2015-08-18 17:41:02.757 [1256862784] nsp.pin.cio.IODevice Module at address 28 is reporting Internal Error Code 32
2015-08-18 17:41:02.825 [1256862784] nsp.pin.cio.IODevice Module at address 12 is reporting Internal Error Code 32
2015-08-18 17:41:02.869 [1256862784] nsp.pin.cio.IODevice Module at address 13 is reporting Internal Error Code 32
2015-08-18 17:41:02.951 [1256862784] nsp.pin.cio.IODevice Module at address 15 is reporting Internal Error Code 32
2015-06-18 10:05:13.912 [1255584832] nsp.pin.cio.CIOException Error: Bad_Address (0xb0000), module Automation_Server_Io_Bus(31), moduleCode 0, dispString "AS address is invalid", techString "nsp_servers/plugins/CentralIOPlugIn/CIO/source/IOManager.cpp line 460"
2015-06-18 10:05:20.789 [1255584832] nsp.pin.cio.IOBus IOBusServer::run: Caught CIO exception from slot 3
Building Operation Automation Server
Warning
One or more terminal base may have to be replaced.
Intermittent IO connection (typically in S-cable).
Follow this document or Blacklisted Device Detected for steps to resolve the problem.
Tags (2)
  • 17968
  • MahmoudSayed22
75% helpful (3/4)