Require an Enthalpy Scheme Program For MicroNet Controllers to give enthalpy value.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Require an Enthalpy Scheme Program For MicroNet Controllers to give enthalpy value.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • Gary
    Gary

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
978 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Require an Enthalpy Scheme Program For MicroNet Controllers to give enthalpy value.

Picard Product_Support
‎2018-09-09 10:03 PM

Issue

The requirement to have an enthalpy value, rather than a digital on or off state via the existing object.

Environment

MicroNet
VisiSat
Bubbleland
Enthalpy logic

Cause

VisiSat's Bubbleland programming area stencil contains an enthalpy object.
This object provide a digital state dependant on comparison.
Depending on the controller type depends on the amount or objects the controller supports.


 

There is not a standard object to provide the enthalpy value.

Resolution

1. A simple bubbleland scheme can be created to provide an approximate value for enthalpy.
In the following example only changing temperature and humidity values are used, for other factors used to calculate true enthalpy use a fixed value. For example the value for pressure used is 1 bar.

A custom object that outputs an enthalpy value can be downloaded below.
For example:

OR

2. Click here to down load this custom object.
The file Enthalpy Custom Object.zip unzips to a folder Satchwell with the necessary files.
Copy the Satchwell folder created to your C:\ drive then the files will be placed  in the correct folders in your VisiSat installation ready to use.

If preferred download the relevant controller type configuration file, and then load the configured scheme with the enthalpy objects into the specific controller.

MN300      MN350

MN440      MN450

MN500      MN550

MN620      MN650

OR

3. A VisiSat project containing each controller type with the enthalpy scheme and the configuration saved under a Configs folder within the project. Click here to download the compressed file containing the project. (4.2 MB)

Labels (1)
Labels:
  • Satchwell MicroNet
Attachments
Enthalpy Custom Object.zip
Custom Enthalpy Scheme 300.zip
Custom Enthalpy Scheme 350.zip
Custom Enthalpy Scheme 440.zip
Custom Enthalpy Scheme 450.zip
Custom Enthalpy Scheme 500.zip
Custom Enthalpy Scheme 550.zip
Custom Enthalpy Scheme 620.zip
Custom Enthalpy Scheme 650.zip
VisiSat 2.1 Enthalpy Scheme.zip
Tags (1)
  • Find more articles tagged with:
  • 5269
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of