Issue
The wrong version of the .xif file is being used.
Environment
- NL220
- LonMaker
- Vista
- LonWorks Device
- XIF
Cause
The numbers/types of SNVTs in the file have changed.
SNVTs have been added to an Xenta 500/700/913.
Resolution
- Ensure that Vista Server is running.
- In Vista System Plug-In, in the LNS Network pane, right-click the LonWorks device object.
- Click Replace
- Click Next
- Keep default neuron ID.
- Click Next
- Select Upload From Device
- Click Next
- Click Ok
- Select the LonWorks device object and check that the SNVTs are available in the object view window