The wrong version of the .xif file is being used.
  • NL220
  • LonMaker
  • Vista
  • LonWorks Device
  • XIF
The numbers/types of SNVTs in the file have changed.
SNVTs have been added to an Xenta 500/700/913.
  1. Ensure that Vista Server is running.
  2. In Vista System Plug-In, in the LNS Network pane, right-click the LonWorks device object.
  3. Click Replace
  4. Click Next
  5. Keep default neuron ID.
  6. Click Next
  7. Select Upload From Device
  8. Click Next
  9. Click Ok
  10. Select the LonWorks device object and check that the SNVTs are available in the object view window