Replacing an MR-VAV-AX
  • Replacing an MR-VAV-AX
  • Derrick_Ratliff
    Derrick_Ratliff
‎2018-09-06 01:40 PM
Procedure for replacing an MR-VAV-AX
I/NET
MR-VAV-AX
Hardware is in need of repair or replacement
  1. Ensure that you have a valid .sav file for the ASC.
  2. Remove defective MR-VAV-AX hardware
  3. Copy DIP switch settings of the old MR-VAV-AX to the new MR-VAV-AX
  4. Re-verify hardware terminations to ensure that wiring did not cause the existing device to need repair
  5. Power up the new MR-VAV-AX
  6. At the I/NET workstation, connect to the appropriate Sub Lan Interface controller.
  7. Select Edit>Controller>ASC Parameters
  8. Click Update ASC
  9. Select the address of the replaced MR-VAV-AX and click OK
  10. Once the download is complete select the address of the replaced MR-VAV-AX
  11. Click Restore
  12. Once the download is complete verify controller function
  • TAC INET