Replacing an Automation Server with an AS-P

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Replacing an Automation Server with an AS-P
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Gary
    Gary
  • Cody_Failinger
    Cody_Failinger
  • HenrikTarpgaard
    HenrikTarpgaard
  • Benji
    Benji
  • AbeMeran
    AbeMeran
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
12298 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Replacing an Automation Server with an AS-P

Picard Product_Support
‎2018-09-10 01:04 PM

Last Updated: Admiral GavinHe Admiral ‎2023-06-12 05:31 AM

Issue

It is not clear how to replace an existing AS with a new AS-P

Product Line

EcoStruxure Building Operation

Environment

  • Automation Server (AS)
  • Automation Server Premium (AS-P)
  • First detected in version 1.7

Cause

Detailed instructions on how to replace an existing AS with a new AS-P are needed

Resolution

WebHelp references

Automation Server Replacement Using Restore

Automation Server Replacement Using Restore Workflow


Overview

Main differences between an AS and an AS-P:

  1. In the AS-P, the RS-485 ports have been re-located to the top.
  2. The AS-P has 2 Ethernet ports; port 2 can be used as a switch only as of SBO version 1.81.
  3. AS-P device USB port format changed to mini USB.
  4. Operator Panel port has been removed.
  5. Hardware factory reset has been removed.
  6. AS-P uses pluggable connectors for field buses. (not shown in picture above)
  7. Consider the power consumption. AS-P requires 10 watts, while the Automation Server only required 7 watts.


Preparations

In preparation for replacing an Automation Server with an AS-P the following considerations must be made:

Power consumption
Since the AS-P consumes three more watts than the classic Automation Server, the power budget needs to be reviewed to check whether an additional power supply and/or rearrangement of the current configuration is needed, if the configuration includes IO modules.

Terminal base
The terminal base for the classic Automation Server can be used with the new AS-P after removal of the upper terminal block. Note though that all field buses wiring has to be moved to the pluggable connectors used with the AS-P.

RS-485 field bus re-wiring
Since the RS-485 ports and connectors have been relocated, the termination at the server of any field bus located on those ports will need re-wiring. Also, the physical specification of the RS-485 port is changed in the AS-P, so review whether the termination resistors needs to be replaced. Refer to Configuration Selection for Generic RS-485 Network Devices

AS-P firmware
Unlike the classic Automation Server, the AS-P ships from the factory with no firmware installed. Make sure to procure the appropriate Device Administrator firmware to install in the unit. First version that supports the AS-P is 1.7. Note once again that the USB port format in the AS-P is mini USB, so procure the appropriate USB cable.

Backup file
Make a backup of the classic AS to be replaced, the AS-P will restore from a classic AS backup but this is a one way process, the classic AS will not restore from an AS-P backup file. If the classic AS is running an older version of firmware, it will have to be upgraded first to at least 1.7.2.


Power budget review

Since the AS-P consumes 10 watts of power versus 7 watts for the classic Automation Server, it is necessary to review the power budget to ensure there is enough power for the AS-P, if the Automation Server being replaced is hosting IO modules.

One power supply (PS-24V) can supply 30W.

The following table shows power consumption for the different device types

Device Power
AS-P 10
AS 7
DO-FA-12-H 1.8
DO-FA-12 1.8
DO-FC-8-H 2.2
DO-FC-8 2.2
DI-16 1.6
RTD-DI-16 1.6
AC-4 11.1
UI-16 1.8
AC-2 5.5
AO-8-H 4.9
AO-8 4.9
AO-V-8-H 0.7
AO-V-8 0.7
UI-8-AO-4 3.2
UI-8-AO-4-H 3.2
UI-8-DO-FC-4 1.9
UI-8-DO-FC-4-H 1.9
UI-8/AO-V-4 1.0
UI-8/AO-V-4-H 1.0


In case one or more additional power supplies are needed, refer to the example given in last part of this article.

 

Note:
The following "replacement procedure" applies to SBO 1.7.x, 1.8x, 1.9x, EBO 2.0x and 3.0.x and 3.1.x.
The AS-P must be running the same version as the original AS backup.
The AS was no longer supported from EBO 3.2.x.
If the site needs to take the AS-P to EBO 3.2 or later, the following should be followed at the AS supported version, then once the AS backup has been restored to the AS-P, the AS-P can be upgraded further, following the supported upgrade path, which can be found in the release notes for the specific EBO version.


 

Replacement procedure

The following procedure assumes the classic Automation Server is being replaced with a brand new AS-P from the factory

  1. If the Automation Server is hosting IO modules then perform the steps in the 'Power Budget' section below before going to the next step.
  2. Perform pre-maintenance procedure per site requirements, i.e. put equipment in hand control mode etc.
  3. Pull out the classic Automation Server from the terminal base. The hardware is designed for hot swapping so there is no need to power down the system.
  4. Remove the terminal block from the terminal base as indicated above.
  5. Insert the AS-P in the terminal base.
  6. Connect Device Administrator to AS-P via USB and install a new database on it. You may want to check the 'Set time on device' check box to initialize the time in the AS-P since its current time is most likely at default if this is a brand new unit or a unit that has been powered down for a while.
  7. Using Device Administrator set the communication parameters of the AS-P (IP address etc) to match the settings of the classic Automation Server being replaced. Connect Ethernet cable from network switch to Ethernet 1 port on the AS-P.
  8. If a hotfix was installed on the Automation Server that is replaced, apply any hotfix needed to match the version of the firmware in the AS-P to the version of the backup from the Automation Server. Since the AS-P should now be able to communicate over IP the application of any HF can be done either over USB or IP.
  9. Using WorkStation, log in directly into the AS-P and restore the backup from the classic AS.
  10. Insert pluggable connectors for field buses.
  11. If there is an Enterprise Server, log into Enterprise Server from WorkStation and verify the newly swapped AS-P is online.
  12. Verify IO modules (if any) are online.
  13. Verify field devices (if any) are online.
  14. Return the system to software control per site requirements.
  15. Verify the system is operating correctly then perform a backup of the AS-P.

Power supply addition example

Consider the following system

If we do the math, the power consumption of this system is 29.8 watts. To avoid exceeding the capacity of the existing PS we need to add an additional PS to the configuration before we replace the Automation Server with an AS-P. In order to maximize the use of the capacity of the first PS we will add a new PS at slot #7 and move the UI8AO4 IO module from slot #7 to slot #8.

 

Steps

  1. Disconnect the UI8AO4 IO module making sure it powers down. It is necessary that any IO modules being relocated on the IO bus are powered down so that they 'forget' their current module IDs. ***
  2. Logon to the Automation Server, make sure UI8A04 shows offline then edit the module and change its Module ID from 7 to 8.
  3. Insert power supply at slot #7
  4. Attach the UI8A04 after the new PS (slot #8), when it powers up it will obtain its new Module ID (8) from the Automation Server.
  5. Last, if the module’s name contains the ID (Slot07:UI8AO4) it may be a good idea to rename it using the new ID to avoid confusion. (Slot08:UI8AO4)

*** It is absolutely necessary that all the modules that will change IDs be powered down, if there are multiple power supplies in the chain make sure to power down all power supplies that are supplying power to any modules that will change slot #.

When removing or inserting IO modules or handling S-Cables, care should be taken not to bend or otherwise damage the pins that connect the module to its IO terminal base, any damage to the pins may cause the module address to shift.

 

Tip

There is a tool on the community (SBO xbk Analyzer) that can be used to automatically calculate the power budget from a backup of the AS/AS-P.

Here is the power budget report generated from the tool after addition of second power supply at slot #7 before replacing the classic AS with an AS-P. The total power consumption is 29.8 watts but we have increased the power capacity of the system to 60 watts with the addition of the second power supply.

 


The instructions above are available as a PDF: Replacing a classic AS with AS-P

Labels (1)
Labels:
  • EcoStruxure Building Operation
Attachments
Tags (4)
  • Find more articles tagged with:
  • 19110
  • GaryMontague23
  • HernanUruena23
  • HernanUruena24
Was this article helpful? Yes No
80% helpful (8/10)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of