Replacement of obsolete Satchwell "AL..S" series Spring Return Linear Actuator by S-E M700 Spring Return Linear Actuator

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Replacement of obsolete Satchwell "AL..S" series Spring Return Linear Actuator by S-E M700 Spring Return Linear Actuator
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2541 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Replacement of obsolete Satchwell "AL..S" series Spring Return Linear Actuator by S-E M700 Spring Return Linear Actuator

Picard Product_Support
‎2018-09-07 08:52 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:56 AM

Issue

Satchwell "AL..S" series Spring Return Linear Actuator requires replacement.

Product Line

Field Devices

Environment

Satchwell “AL..S” series Spring Return Linear Actuator installed on Satchwell MJF, MZ, MZF, VJF, VSF, VZ or VZF series Plug and Seat Valve Body. 

Cause

Obsolescence of Satchwell “AL..S” series Spring Return Linear Actuator.

Resolution

  1. Replace Satchwell ALMS Actuator with S-E M700 Actuator.
    The S-E M700 Actuator may be used to replace an existing Satchwell ALMS Actuator.
    It should be noted however that the S-E M700 Actuator is suitable for use with 24 volt power supplies only, while the Satchwell ALMS Actuator is a mains voltage device.
    The S-E M700 Actuator has an average power consumption of 30 VA and the use of an independent 230 / 24 volt Transformer rated 50 VA is recommended.
     S-E Transformer Type TR60 (341-3060-000)
     
  2. Replacement of Satchwell ALXS Actuator with S-E M700 Actuator.
    The S-E M700 Actuator may be used to replace an existing Satchwell ALXS Actuator.
    It should be noted however that where an existing Satchwell ALXS Actuator has been connected to a Satchwell Climatronic Controller via an independent Transformer, it is probable that the Transformer will have been rated to provide the level of power required by a single ALXS Actuator (23VA) In such circumstances the existing independent Transformer may also require replacement by another independent Transformer, rated to provide the greater level of power required by a single S-E M700 Actuator (50VA)
    S-E Transformer Type TR60 (341-3060-000)
     
  3. Replacement of Satchwell ALES Actuator with S-E M700 Actuator.
    The S-E M700 Actuator may be used to replace an existing Satchwell ALES Actuator.
    It should be noted however that where an existing Satchwell ALES Actuator has been connected to a Satchwell Climatronic Controller via an independent Transformer, it is probable that the Transformer will have been rated to provide the level of power required by a single ALES Actuator (26VA) In such circumstances the existing independent Transformer may also require replacement by another independent Transformer, rated to provide the greater level of power required by a single S-E M700 Actuator (50VA)
    S-E Transformer Type TR60 (341-3060-000)
     

Please check the latest catalog for current equipment.

Labels (1)
Labels:
  • Field Devices
Tags (1)
  • Find more articles tagged with:
  • 4905
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore