Replacement of Satchwell "AMS" series Spring Return Rotary Actuator
  • Replacement of Satchwell "AMS" series Spring Return Rotary Actuator
‎2018-09-10 12:05 AM
Last Updated: Crewman ContentModerator ‎2025-09-25 02:56 AM
Satchwell "AMS" series Spring Return Rotary Actuator requires replacement by S-E M700 Spring Return Linear Actuator due to obsolescence. (Actuator Wiring)
Field Devices
  • Satchwell “AMS” series Spring Return Rotary Actuator installed on Satchwell MJF, MZ, MZF, VJF, VSF, VZ or VZF series Plug and Seat Valve Body.
  • N.B.
  • Where a Satchwell "AMS" series Spring Return Rotary Actuator is installed on a Satchwell VV Butterfly Valve Body then NO simple Actuator replacement is available.
  • Please refer to Replacement of Satchwell "AMS" or "AMSH" (high torque) series Spring Return Rotary Actuator
Obsolescence of Satchwell "AMS" series Spring Return Rotary Actuator.
Replace Satchwell AMS Actuator with S-E M700 Actuator.
The S-E M700 Actuator may be used to replace an existing Satchwell AMS Actuator.
It should be noted however that the S-E M700 Actuator is suitable for use with 24 volt power supplies only, while the Satchwell AMS Actuator is a mains voltage device.
The S-E M700 Actuator has an average power consumption of 30 VA and the use of an independent 230 / 24 volt Transformer rated 50 VA is recommended.
S-E Transformer Type TR60 (341-3060-000)
Please check the latest catalog for current equipment.
  • Field Devices
  • 5429