Replacement of Satchwell "AMS" or "AMSH" (high torque) series Spring Return Rotary Actuator

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Replacement of Satchwell "AMS" or "AMSH" (high torque) series Spring Return Rotary Actuator
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1986 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Replacement of Satchwell "AMS" or "AMSH" (high torque) series Spring Return Rotary Actuator

Picard Product_Support
‎2018-09-10 12:04 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:55 AM

Issue

Satchwell "AMS" and "AMSH" series Spring Return Rotary Actuator requires replacement by S-E M700 Spring Return Linear Actuator due to obsolescence.

Product Line

Field Devices

Environment

  • Satchwell "AMS" series Spring Return Rotary Actuator installed on Satchwell MJF, MZ, MZF, VJF, VSF, VZ or VZF series Plug and Seat Valve Body.
  • Satchwell "AMSH" series Spring Return Rotary Actuator installed on Satchwell MZF or VZF series 125mm and 150mm Plug and Seat Valve Body.
  • N.B.
  • Where a Satchwell "AMS" series Spring Return Rotary Actuator is installed on a Satchwell VV Butterfly Valve Body then NO simple Actuator replacement is available.
  • See Replacement of Satchwell V V series Butterfly Valve Body

Cause

Obsolescence of Satchwell AMS and AMSH series Spring Return Rotary Actuator.

Resolution

  1. The new actuator is 24Vac and the control signal will need to be converted from 230Vac to 24Vac, this could be achieved by a transformer and 2 off 230Vac relays. The old signals switch the coils of the relays. The relay contacts switch 24Vac to the new actuator.
  2. Replace Satchwell AMS or AMSH series Spring Return Rotary Actuator with S-E M700 Spring Return Linear Actuator and Linkage Kit:
    AMS = M700 + L7SV (880-0126-000) Linkage Kit.
    N.B.
    M700 is available with two different spring return actions
    M700 - SRSU (880-0430-000) = Spring Return Spring Up          ( M700 - SRSU will CLOSE a Satchwell Valve.)
    M700 - SRSD (880-0440-000) = Spring Return Spring Down     ( M700 - SRSD will OPEN a Satchwell Valve.)
  3. Should the Satchwell AMS series Actuator include a wired Auxiliary Switch then the following S-E M700 Actuator specifications which include 2 independent 24 volt 4 amp AC-1 rated SPDT Auxiliary End Point Switches should be considered as appropriate:
    M700 - S2 - SRSU (880-0431-000)
    M700 - S2 - SRSD (880-0441-000)
  4. Alternatively Auxiliary Switch Pack S2 (880-0104-000) - Two independent 24 volt 4 amp AC-1 rated SPDT Auxiliary End Point Switches may be purchased separately permitting local installation.
  5. Particular care should be taken when selecting a TAC Forta M700 Spring Return Actuator to replace an existing Satchwell AMS Spring Return Actuator.

Please refer to Replacement of Satchwell "AL..S" series Spring Return Linear Actuator.

Please check the latest catalog for current equipment.

Labels (1)
Labels:
  • Field Devices
Tags (4)
  • Find more articles tagged with:
  • 5428
  • ams2201
  • ams2202
  • ams2251
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore