Replacement of Satchwell ZRM series or AZ2451 Rotary Actuator due to obsolescence.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Replacement of Satchwell ZRM series or AZ2451 Rotary Actuator due to obsolescence.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidChild
    DavidChild
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1935 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Replacement of Satchwell ZRM series or AZ2451 Rotary Actuator due to obsolescence.

Picard Product_Support
‎2018-09-06 02:02 PM

Issue

Satchwell ZRM series or AZ2451 Rotary Actuator requires replacement..

Environment

Satchwell ZRM Rotary Actuator installed on Satchwell MB Series Rotary Shoe Valve Body.

Satchwell AZ2451 Rotary Actuator installed on Satchwell MB Series Rotary Shoe Valve Body.

Satchwell ZRM Rotary Actuator installed on Satchwell MC Series Step Controller.

Satchwell ZRM Rotary Actuator installed on Satchwell MD Series Step Controller.

Cause

Obsolescence of Satchwell ZRM series and AZ2451 Rotary Actuator

Resolution

Please check number of wires connected to ZRM Actuator as this will assist in determining a suitable replacement.

The Satchwell ZRM Actuator or AZ2451 would normally have been installed on a Satchwell MB Valve Body.

The Satchwell ZRM Actuator could however have been installed on a Satchwell MC or MD Series Step Controller.

The Actuator comprised a 6 wire electrical connection enabling it to be operated from a Satchwell Z Monotronic or CZT Climatronic Proportional Controller as follows :- 

Terminal 1 – Open signal

Terminal 2 – Close signal

Terminal 3 – Common 

Terminal A – 135 ohm Feedback Potentiometer – winding

Terminal B – 135 ohm Feedback Potentiometer – wiper

Terminal C – 135 ohm Feedback Potentiometer – winding

1. If all 6 wires are connected then the ZRM Actuator or AZ2451 may be replaced by one or other of the following SE Actuators :-

MD20B-24 + Linkage Kit 914-1071-000 from Schneider Electric and an accessory kit  P140A from Belimo

2. ALTERNATIVE REPLACEMENT If in some installations, 3 wires are only connected to the ZRM Actuator.

Terminal 1 – Open signal

Terminal 2 – Close signal

Terminal 3 – Common

In such instances the ZRM Actuator or AZ2451 may be replaced by the XRM3201 or MD10B-24/MD20B-24 + Linkage Kit 914-1071-000

Labels (1)
Labels:
  • Field Devices
Tags (1)
  • Find more articles tagged with:
  • 4768
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore