Replacement of Satchwell CZU Mk 1 Zonemaster Controller by S-E Satchwell CZU Mk 4 Zonemaster Controller due to obsolescence.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Replacement of Satchwell CZU Mk 1 Zonemaster Controller by S-E Satchwell CZU Mk 4 Zonemaster Controller due to obsolescence.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3918 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Replacement of Satchwell CZU Mk 1 Zonemaster Controller by S-E Satchwell CZU Mk 4 Zonemaster Controller due to obsolescence.

Picard Product_Support
‎2018-09-10 02:47 AM

Issue

Satchwell CZU Mk 1 Zonemaster Controller requires replacement.

Environment

  • Stand alone Fan Coil Unit Temperature Controller.
  • Satchwell CZU Mk 1 Zonemaster Controller.
  • CZU 1201
  • CZU 1202
  • CZU 1203

Cause

Obsolescence of Satchwell CZU Mk 1 Zonemaster Controller.

Resolution

OVERVIEW

Replacement of Satchwell CZU Mk 1 Zonemaster Controller with S-E Satchwell CZU Mk 4 Zonemaster Controller.

The CZU 4201 may be used to replace the following CZU Mk 1 Controllers :-

CZU 1201, CZU 1202, CZU 1203

N. B.

CZU 1201 Controllers provided an additional -9 to +9 V d.c. output enabling connection to peripherals such as the Satchwell NSU 1401 Night Set-back Override Unit, TSU 1402 Two Step Auxiliary Unit and SSU 1403 Signal Selector Unit.

CZU 1202 and CZU 1203 Controllers provided an additional -0.5 to +9 or -9 to +0.5 V d.c. output enabling connection to the Satchwell NSU 1401 Night Set-back Override Unit.

Additional outputs are not provided on the CZU 4201 Controller and in those applications where these are required then it will be necessary to consider an alternative Controller to the CZU 4201.

Details of the CZU 4201 may be viewed here.

 

CZU Mk 1 CONTROLLER - INTEGRAL TEMPERATURE SENSOR APPLICATION

CZU Mk 1 Controllers were manufactured with an integral Temperature Sensor.

Adjustment of setpoint was undertaken by means of a dial mounted on the front of the Controller housing.

This enabled the Controller to be installed in the controlled space.

The CZU 4201 however is intended to be installed either in or on a Fan Coil Unit casing or in a ceiling void.

No setpoint dial is mounted on the front of the CZU 4201 housing, thus precluding installation of the Controller in the controlled space.

Where an existing CZU Mk 1 Controller is installed in the controlled space and is to be replaced, it will be necessary to install an Adjustable Room Temperature Sensor in the controlled space in order that a CZU 4201 may be utilised as a replacement.

The S E STR 612 Adjustable Room Temperature Sensor may be utilised for this purpose.

Details of the STR 612 may be viewed here.

Any existing Actuator / Valve Body assemblies connected to the CZU Mk 1 Controller may be retained for connection to the CZU 4201.

 

CZU Mk 1 CONTROLLER - EXTERNAL TEMPERATURE SENSOR APPLICATION

In some instances an existing CZU Mk 1 Controller may have been installed with its integral Temperature Sensor disabled.

In such instances a remote Satchwell Adjustable Room Temperature Sensor such as the DRT 3451, or a remote Satchwell Duct Temperature Sensor from the DDU range of Sensors may have been installed and connected to the Controller..

Any existing remote Satchwell Temperature Sensors may be retained for connection to the CZU 4201.

Should the remote Satchwell Adjustable Room Temperature Sensor require replacement then this may be replaced by an S E STR 612 Adjustable Room Temperature Sensor.

Details of the STR 612 may be viewed here.

Should the remote Satchwell Duct Temperature Sensor require replacement then this may be replaced by an S E STD 670 Duct Temperature Sensor.

Details of the STD 670 may be viewed here.

Labels (1)
Labels:
  • Field Devices
Attachments
Tags (1)
  • Find more articles tagged with:
  • 6041
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore