Replacement of M42 series actuators
  • Replacement of M42 series actuators
  • SESA150559
    SESA150559
‎2018-09-06 11:07 AM
With the M42 series actuators being obsolete, they need to be replaced.
M42
Actuator M42/230 8401000000
Actuator M42/230 8401300000
Actuator M42P/24 8402100010
Actuator M42PBB/24 8402400010
TAC Forta series
M9/EM9
Replacement of obsolete actuators.
Spare part for actuator for valves with linear moving stem the complete actuator TAC Forta should be used.
When a 230 Volt actuator is requested the TAC forta needs a supplementary 230/24 Volt transformer.
Depending on the electrical installation certain modifications may be necessary.
For valves with rotating stem, actuators M9/EM9 can be used.