Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Replacement for the ZVX 4302

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Replacement for the ZVX 4302
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3479 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Replacement for the ZVX 4302

Picard Product_Support
‎2018-09-10 01:43 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:06 AM

Issue

Replacement of Obsolete ZVX 4302 , ZVX4302, ZVX-4302

Environment

site with ZVX 4302 that needs to be replaced

ZVX4301

ZVX4302

ZVX4303

Cause

Obsolete ZVX 4302 valve , T-type, 3port, 230V with Actuator, screwed, 3/4 inch size. The ZVX 2-port Flow Control and 3-port Diverter Valves are for the regulation of low pressure heating and chilled water circuits where on/off control is required.

Resolution

The Satchwell ZVX 4202 was just one specification among many of similar ZVX series Zone valves.

Details of the complete range of ZVX 2-port and 3-port Zone Valves from the Satchwell “Options” range appear in the pdf attached in the link at the bottom of this article (pdf).

The ZVX range of Zone Valves were “badged” Satchwell and, to the best of my knowledge, were of ORKLI manufacture. Please note at the present (2011) there is no direct replacement for the Satchwell ZVX series of Zone Valves. This may require the pipe and fittings to be replaced or altered.

At present the replacement for the Satchwell ZVX range of Zone Valves still appears to be the ERIE VT range of Valve Bodies and ERIE AG/AH range of Actuators.

Replacement details are included in the following extract from an earlier cross-reference document produced by Gina Kimmins whilst in the Product Sales division of TAC / Satchwell

WHEN ORDERING BODY & ACTUATOR TOGETHER, DROP THE "A" FROM THE ACTUATOR EG. VT2231G13A230 AND USE THIS PART NUMBER TO ORDER

 

Here is the documentation for the Satchwell ZVX 2 port and 3 port zone valves.

VT Valve Body and AG / AH Actuator that currently replace the ZVX ERIE POP TOP Datasheet and ERIE POP TOP Install Guide

Labels (1)
Labels:
  • Field Devices
Attachments
Tags (4)
  • Find more articles tagged with:
  • 6072
  • zvx4301
  • zvx4302
  • zvx4303
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore