Replacement for V395-1 valve
  • Replacement for V395-1 valve
  • SESA150559
    SESA150559
‎2018-09-06 12:26 PM
The V395-1 is obsolete and no longer available
V395:
7319501000
7319505000
7319509000
7319513000
7319515000
7319519000
V321:
7312153010
7312157010
7312161010
7312165010
7312169010
TAC Forta
The V395 valve is obsolete and no spare parts or direct replacement valves are available.
The closest suitable valve is the V321 with a Forta actuator. The "A to AB" measurements are the same, but the "A-AB centerline to B flange" is different. Double check the data sheets for more information and details.
Keep in mind that V395-1 is PN25, while the V321 is PN16.