Replace Invensys Actuator Model MA5-419-500-0-3
  • Replace Invensys Actuator Model MA5-419-500-0-3
  • sesa139513
    sesa139513
‎2018-09-10 01:43 AM
Damper Control Actuator site
Replacement Specifications for Obsolete Invensys MA5-419-500 which is a Two Position Damper Actuator, SR, 240V, 50 Hz, 60 lb-in, w/SPDT Aux. Switch
The closest replacement would be the MD5B-24(-S)/-230(-S) On/Off or 3-point 24 V AC/230 V AC Damper Actuator 5 Nm (45 in-lb).
Note: This is a Rockford, Illinois offering, which we would not normally have offered this in Europe in the past.
There is a range of Non-Spring Return Damper Actuators detailed in Pages 54 and 55 of the below Schneider Electric Catalogue.
Similarly there is a range of Spring Return Damper Actuators detailed in Pages 56 through 58 of the below Schneider Electric Catalogue.
Damper Actuator Accessories are shown on Page 59 of the below Schneider Electric Catalogue.
Schneider Electric HVAC Valve and Actuator Catalogue
  • Field Devices
  • 6071
0% helpful (0/1)