Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Remote Alarm Manager running on a Vista server running in 30 day demo mode..

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Remote Alarm Manager running on a Vista server running in 30 day demo mode..
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • Gary
    Gary
  • sesa119747
    sesa119747
  • DavidFisher
    DavidFisher

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1000 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Remote Alarm Manager running on a Vista server running in 30 day demo mode..

Picard Product_Support
‎2018-09-10 11:14 PM

Issue

Remote Alarm Manager running on a Vista server loses license.

Environment

RAM

Remote Alarm Manager

License entitlement

Cause

There are two issues here.
Issue one:

Remote alarm manager running with TAC Vista
Occasionally (2- 4 weeks) the Remote alarm manager indicates a temporary read error of the TAC license server.
This can be seen as: -
Unable to check out a licence
Dongle failure 30 day limited mode entered - expires **/**/**** *:**:**
This in itself is a minor issue but when combined with the second issue has a major impact on the operation on site.

Issue two:

Remote alarm manager running with TAC Vista
Remote alarm manager fails to recover after its license management briefly loses a valid license from the TAC license server.
Remote alarm manager doesn't recover
This can be seen repeated in RAMs database as: -
Checking for TAC Licence Server.
Checked out a single licence OK
Licence state - 1 interface(s) in demo

 

Resolution

Contact Product Support and provide the following information:

To facilitate a quick solution for this issue please supply the following details: -

  1. Site company name and address
  2. Copy of the original Remote Alarm Manager registration form.
  3. Copy of TAC license entitlement form.
  4. Confirmation of Vista version installed.
  5. Confirmation of Remote Alarm Manager version installed.
  6. Type of installation (engine, interface and consul ((installed on Vista server or remote) 
  7. The computer operating system for the R.A.M./Vista installation.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 8064
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of