Recovery of an I.LON 1000 in the boot state.
  • Recovery of an I.LON 1000 in the boot state.
  • SESA116857
    SESA116857
‎2018-09-06 03:12 PM
i.LON 1000
The router has become corrupt.
If the system image on an I.LON 1000 has become corrupt and the device enters a boot state when powered up then the following steps should be taken to correct it:
  1. Download the system image found in the "C:\Lonworks\iLON\Images\iLON x.xx" directory using an FTP client.
  2. Connect to the device with the serial cable and issue the "format" command. After the command has completed retry step 1.
  3. If neither of the previous methods worked, connect to the device with the serial cable and issue the "factorydefault" command. This should restore the device to how it came out of the box.
  • 1700