Issue
While Running I/NET Seven Rev 1.17 and above a new SCU is added to replace an existing DPU. "Software Restore" was run by mistake, and the SCU no longer works.
Product Line
TAC INET
Environment
I/NET site
Cause
"Software Restore" was run by mistake
Resolution
Please use the following document link: How to load SCU1284 BINS.doc