Receiving Xenta Server trend log data without TAC Vista

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Receiving Xenta Server trend log data without TAC Vista
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2223 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Receiving Xenta Server trend log data without TAC Vista

Picard Product_Support
‎2018-09-10 10:18 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:55 AM

Issue

  • Is there any way to get the Xenta Server trend log data without TAC Vista?
  • How to get the Xenta Server trend log values from the web interface
  • How to e-mail the Xenta Server trend log values

Product Line

Satchwell MicroNet, TAC Vista

Environment

  • TAC Xenta Server
  • TAC Xenta 511, 527, 555
  • TAC Xenta 711, 731

Cause

The TAC Xenta Server is installed standalone and TAC Vista can not be used to view or save the trend logs.

However if you want to collect and store data from multiple trend logs on a regular basis we do strongly recommend using TAC Vista.

Resolution

There are two ways to get the trend log data from a Xenta Server (except for TAC Vista):

1. Manually copy the trend log values from the Xenta Server web interface

  • In XBuilder, create a trend log page and drag the trend log to it
  • Log in to the web interface and go to the trend log page
  • Right click the trend log signal name and choose "view values"
  • Copy/paste the values to for example Excel.
     

2. Forwarding the trend log data as an e-mail

  • First make sure that the SMTP settings in XBuilder are correct. For troubleshooting on this, see Troubleshooting sending emails from a Xenta Server
  • Create a receiver group and define one or more e-mail addresses to receive the trend log data.
  • Highlight the trend log. 
  • Under Log Data Transfer Settings, click the Receiver Group box, and select the Receiver Group list.
  • In the Subject box, type a suitable subject. If desired, also type a suitable text in the Body box.
  • In the Log Events Included box, click Yes to attach log events to the e-mail message.
  • You must also specify when the log data is forwarded. For this, create a time object which you drag to the "send data" signal on the trend log.
  • When the trend log data is forwarded, the receiver group e-mail addresses will receive the trendlog data as an attached .log file.

For more information, see chapter 8.2.2. in the TAC Xenta Server – Web Server, Technical Manual

Labels (2)
Labels:
  • Satchwell MicroNet
  • TAC Vista
Tags (3)
  • Find more articles tagged with:
  • 7679
  • export
  • extract
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore