Received error on CX reload "Infinity controller error: Copy protection violation has occurred"
  • Received error on CX reload "Infinity controller error: Copy protection violation has occurred"
  • Carl_Slack
    Carl_Slack
‎2018-09-06 02:14 PM
CX 99xx model controllers
Continuum Cyberstation
Flashing the controller with the wrong flash file will cause the error "Infinity controller error: Copy protection violation has occurred"
When selecting the firmware to flash to your controller, there is are two versions for each CX99 controller. If you are not using SNMP alarming uprev your firmware to the "SNMP Not Set" version.