Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Reassigning a USB Serial Adaptor to a desired COM port

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Reassigning a USB Serial Adaptor to a desired COM port
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Sacco
    Sacco
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2368 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Reassigning a USB Serial Adaptor to a desired COM port

Picard Product_Support
‎2018-09-06 02:26 PM

Issue

  • Reassigning a USB Serial Adaptor to a desired COM port
  • Reassigning a USB to DB-9 Adaptor to a desired COM Port

Product Line

TAC Vista

Environment

Windows OS

Cause

It is common for newer laptops to come without DB-9 serial connections. USB to DB-9 adaptors have to be used instead. When this USB device is installed, Windows will allocate the first COM port available in the system. In most cases, this will not be COM1, which is the default port designation for both Menta and the Download Wizard. If COM10 or greater is assigned, then it cannot be used with Menta for a direct download because Menta's COM port designation drop-down list only goes to COM9.

Resolution

Reassign the USB to DB-9 adaptor to the desired COM port:

  1. Right-click on My Computer and select "Manage"
  2. In the left pane of the Computer Management Console, select Device Manager. This will populate the right pane with system information.
  3. Expand "Ports (COM & LPT)." There will be a list of ports in use and which device is associated to the COM port.
  4. Look for the USB to Serial Bridge (COMx). If the USB to DB-9 adaptor is not assigned to the desired COM port, right-click on it and select "Properties."
  5. From the Port Settings tab, select "Advanced."
  6. In the Advanced Settings is a drop-down menu for assigning the COM port number to this device. Select the desired COM port.
    1. If it is noted that the COM port is "(in use)," find the device using that port
    2. Reassign that device to another open port.
    3. This will free up the desired COM port for the USB to DB-9 adaptor.
  7. Changing COM port may take some time for Windows to process and put into effect. Monitor "Ports (COM & LPT)" in the Computer Management Console. This will show the reassigned COM port when the operation has finished.

*it is also possible to assign to a port in use which should move the previous device to another com, however this should be used as a last resort.

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 3954
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of