Ramp/Timer Calc
  • Ramp/Timer Calc
  • sesa139513
    sesa139513
Ramp/Timer Calc
‎2018-09-06 03:07 PM
Ramp/Timer Calc
I/NET Seven Site
application that requires a calculation that will ramp up automatically or use a Timer
Do you have an application that requires a calculation that will ramp up automatically or use a Timer? Take a look at these and see if it will fit:
Ramp Scan Rate 10 = 600 sec Ramp Time
LOW((L0+C0)*(L1>C0),C1)
C0: 1
C1: 100
L0: Output from O/A Time Delay Output
L1: Module Output
Timer Scan Rate 60 seconds
LOW((P0+C0)*(P1|(P0>=C0&P0
P0: Timer output
P1: Timer start
C0: Increment (1=1 minute increments)
C1: High Limit (30=30 minute timer)
  • TAC INET
  • 1914