RP-C Controller Type Change Due to STM32 Flash Corruption

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • RP-C Controller Type Change Due to STM32 Flash Corruption
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • David_Purser
    David_Purser

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
195 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

RP-C Controller Type Change Due to STM32 Flash Corruption

Picard David_Purser Picard
‎2025-09-30 10:38 AM

on ‎2025-09-30 10:38 AM

Issue

During or immediately after a firmware upgrade, the RP-C controller may experience corruption of the STM32 processor's flash memory. This results in the controller misreporting its model type and becoming non-functional.

Affected RP-C controllers may exhibit the following:

  • Incorrect controller model appears during BACnet discovery or in the device report.
  • Controller defaults to RP-C-16A-F-230V when STM32 is unresponsive.
  • No communication between STM32 and main processor (LCES).
  • Controller reset button has no effect (no LED blink sequence).
  • Even if the actual model is RP-C-16A-F-230V, it will not operate correctly if STM32 is corrupted.
  • Lack of response to the reset button is a key indicator of STM32 corruption.

Product Line

EcoStruxure Building Operation

Environment

  •  Room Controller (RPC)

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.

Cause

STM32 flash corruption is caused by interruptions during firmware activation, such as:

  • Power cycling the controller before activation completes.
  • Network disruptions during upgrade.
  • Premature assumption that upgrade is complete based on “100%” progress bar.

Resolution

To prevent the issue, perform the following:

  • Do not disturb controller operation during firmware activation.
  • Ensure the following indicators are met before removing power:

    • Firmware revision is updated in the “Firmware revision” column.

    • “Upgrade status” shows Operational.

    • Controller is Online (not just showing 100% progress).

If STM32 corruption has occurred, follow these steps to restore the RP-C controller:

  1. Ensure prerequisites for your laptop:
    • Enterprise Server with Demo License running 5.0.2.109 or higher
    • EBO Workstation compatible with Enterprise Server version
    • instructions are for DHCP network that laptop and controller are connected. Adapt for direct connection using Auto IP, if needed.
    • Multiple SpaceLogic firmwares, as needed to use one different from the version the controller is currently running
  2. Launch EBO Workstation and log into Enterprise Server.
  3. Connect RPC to network via Ethernet.
  4. Apply 24VAC power to RPC.
  5. Open Device Discovery and initiate BACnet discovery using Discover All button.
  6. If RPC is not discovered, cycle power and retry discovery.
  7. Once discovered (likely as RP-C-16A-F-230V), host it to the ES IP network.
  8. Ensure ES has a different firmware version than the one currently on RPC.
  9. Go to Firmware Upgrade screen:
    • Select a different firmware version.
    • Choose Activate Immediately.
    • Click OK to start upgrade.
  10. Wait for the status to change:
    • “Download firmware in progress” → “Activate firmware scheduled” → “Activate firmware in progress”.
  11. RPC will go offline in 1–3 minutes.
  12. Wait 1 minute, then power cycle RPC (off for 5 seconds, then on).
  13. Wait another minute, then repeat power cycle.
  14. Within 10–30 seconds, Status LED flashes Red & Green (STM32 reprogramming is being performed).
  15. After ~1:15 minutes, LED flashes White & Green, then toggles Red & Blue (Bluetooth FW upgrade is being performed).
  16. There is an expected white and green flash of LED where the final LED state is Solid Green.
  17. Rediscover RPC in EBO.
  18. The controller should now report the correct model and be fully operational.
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • DavidPurser25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore