PxInclude with Scheduler can cause the G3 Workbench application to lockup
  • PxInclude with Scheduler can cause the G3 Workbench application to lockup
‎2018-09-07 01:57 PM
Last Updated: Crewman ContentModerator ‎2025-09-25 02:55 AM
Changing between view and edit modes using Workbench after adding a PxInclude object to a parent px file with a schedule causes Workbench to lockup and fail. A restart of the Workbench application is required.
TAC I/A Series G3 ENC-410, ENC-520, and Enterprise Network Server
Workbench failed to process the scheduler within the PxInclude.
The issue has been resolved in bajaUi module versions 3.3.34.2, 3.4.64.1, 3.5.34.1 and higher.  The files, bajaui 3.3.34.2 is available for download from The Exchange Download Center.
  1.  Download the bajaUi version zip file for the required G3 build.
    Caution: Always backup the station database before performing any upgrade.
  2. If Enterprise Network Server, stop running station and close the Workbench application.
  3. Extract the file and replace the existing bajaUi jar file in the appropriate modules directory of G3.
  4. Start Workbench and start station if Enterprise Network Server. Use the Workbench Platform Software Manager to the upgrade the bajaUi module in ENCs as required.