Putting I/O into Forced-By-Operator Override from live, directly connected Menta

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Putting I/O into Forced-By-Operator Override from live, directly connected Menta
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1430 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Putting I/O into Forced-By-Operator Override from live, directly connected Menta

Picard Product_Support
‎2018-09-06 02:18 PM

Issue

When directly connected to a Xenta programmable controller through a serial cable, and observing live Menta, it is possible to override inputs and outputs.  This override is the same override attribute that can be set from the OP and from the Workstation.

Environment

  • Menta
  • Xenta programmable
  • Xenta 280, 281, 282, 283, 300, 301, 302, 401, 401:B

Cause

Overriding points while simultaneously witnessing live updates of all program values is an effective troubleshooting technique.

Resolution

Directly connect live to a Xenta Programmable

  1. Download the correct Menta file to the hard drive of a laptop.
    1. Right click on the controller in Workstation and select Edit.
    2. File > Save As ... to the hard drive.
    3. The Menta file must exactly match what currently is downloaded into the controller or else it won't connect.
  2. Connect to the RS-232 port on the face of the Xenta programmable.
  3. Open the Menta file.
  4. Options > Simulate
  5. Click the Online button in the top left corner.
  6. Select "Connect" from the menu.

View I/O and override

  1. Options > I/O Configuration
  2. This brings up a list of all inputs and outputs in the controller.  The last column says "Not overridden" for any point not currently overridden.  If it is, it will show the override value.  Choose a point and click the Override button at the bottom.
  3. Check the box to override and enter the desired value.  Click OK.
  4. The point is now in override.

NOTE: This override attribute is the same override that is available through the OP and through Vista Workstation.  Points can be put into override and taken out of override from any of these 3 locations and it will dynamically update any other concurrent users.

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 4301
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of