Issue
- Will public signals in TAC Xenta show up in Echelon Lonmaker?
- Will AI, DI, AO, DO, PVR, PVI, PVB blocks show up in Echelon Lonmaker?
Product Line
TAC Vista
Environment
- TAC Menta
- LonMaker or NL220
- Xenta 30x, 401, 28x
Cause
Public signal are proprietary and can only be viewed from Schneider Electric products such as TAC Vista Workstation or EcoStruxure Building Operation.
Resolution
The answer to both questions is no. Only SNVTs are displayed in Echelon Lonmaker, and the SNVTs have to be added in TAC Menta and then downloaded to the TAC Xenta devices.