Issue
Protect DCUs and PCUs from sensors shorts
Environment
- DCU
- PCU
Cause
If Distributive Control Units (DCUs) and Process Control Units (PCUs) have sensors in critical areas and one of the sensors shorts, it may affect the readings of the other sensors on the controller.
Resolution
Isolate the input signal into the controller:
- Add an in-line 20 milliamp fuse or circuit breaker
- Use an Isolated DC to DC transmitter. For an example of such a device go to the Kele 2000/ 2001 Parts Catalog, model DT13, or go to their web site www.kele.com, or call them at 901-937-4900, International 901-382-6084.