Process to use I/NET Encryption feature to encrypt an existing network or segment of network

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Process to use I/NET Encryption feature to encrypt an existing network or segment of network
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1322 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Process to use I/NET Encryption feature to encrypt an existing network or segment of network

Picard Product_Support
‎2018-09-06 01:22 PM

Issue

Process to use I/NET Encryption feature to encrypt an existing network or segment of network

Environment

I/NET

Cause

I/NET system contains or protects items that need addition security or separation from other I/NET networks.

Resolution

To encrypt the Xenta 527 and Host network

 

Important:

********** The Unencrypted and Encrypted UDP ports should be different from each other     (Ex. Unencrypted: 50069, Encrypted: 49152)

********** The Unencrypted UDP port for all routers and workstations should be the same (Ex. Routers: 50069, Workstations: 50069)

********** The Encrypted UDP port for all routers and workstations should be the same (Ex. Routers: 49152, Workstations: 49152)

********** The Encrypted password for all routers and workstations should be the same (Ex. Routers: Test, Workstations: Test)

 

  1. Choose an unencrypted UDP port, either default 50069 or a number between 49153-65535
  2. Set the workstation Advanced IP UDP setting to the chosen unencrypted port
  3. Shutdown I/NET, Shutdown I/O Server(make sure I/O server is shut down) <-check Task Manager to see if all I/NET services are shutdown
  4. Bring all new 527 routers online within the network
  5. Log into the 527 web interface, go to I/NET configuration profile
  6. Set 527 UDP to the chosen unencrypted port you chose in step 1, set the host reference to the workstation IP that is the filemaster/standalone
  7. Save and Restart 527, restart I/NET Filemaster/Standalone
  8. Bring up NP routers under I/O server, check if all routers in the network have appeared in the list
  9. If not all routers have appeared in the list check the unencrypted udp port of the workstation and 527 udp port match
  10. Once all routers have appeared in the online list, click on each router and modify its Advanced IP settings
  11. Check mark the Enable Encryption box, the default encryption port is 49152, make sure you leave the encryption port default or choose an encryption port that will be the same for all routers
  12. Enter a password for encryption(Ex. Test), make sure the password is the same password for each router
  13. Click OK, the router should restart with the new encrypted settings
  14. Repeat steps 10-13 on all routers within the list
  15. All routers should disappear one by one from the Online list as you enable encryption on each router and OK the settings change
  16. Under the main IO configuration screen click on Advanced IP
  17. Check mark the Enable Encryption box, the default encryption port is 49152 or choose the encryption port that corresponds to the same exact encryption port you choose for the routers
  18. Enter in the password for encryption exactly as was done for the routers
  19. Click OK, Click OK on the main screen to save the settings
  20. Shut down I/NET, Restart I/O Server(make sure I/O server is shut down)
  21. Restart I/NET
  22. Open up IO configuration once logged in
  23. Click on NP Routers
  24. The routers you have encrypted should appear back onto the Online list
  25. Troubleshoot: If the routers you have do not appear back onto the list, check each router’s web interface and make sure that the UDP port is set to the encrypted port. If the routers come back but there Name appears as numbers (Ex. 1023,1124) then what happened is the routers are encrypted but the host workstation cannot understand the encryption. To undo everything and start over uncheck encryption on the host workstation and then login to each of the router’s web interface and reset the UDP port to the default I/NET port. Make sure to restart I/O server to make changes take affect.
  26. Test the encryption by having standalone machines and other filemasters not on the same encrypted port try to pull up the routers either by NP routers in IO configuration or Host->Netcon, they should not be able to see any of the routers/host workstations that were encrypted.

 

 

To add a 527 to an existing encrypted network

 

  1. Bring the router online on the chosen unencrypted port
  2. Shutdown I/NET and I/O server
  3. Modify IO configuration
  4. Uncheck enable encryption on host settings Advanced IP
  5. Make sure the unencrypted port is the same port with the router you are bringing online
  6. Shutdown I/NET and I/O server and then restart I/NET
  7. Modify the active IO configuration, under NP routers you should be able to see the new router but none of the old encrypted routers
  8. Modify the new router’s Advanced IP settings
  9. Enable encryption on the new router and assign it the default/chosen encrypted port and enter in the chosen password for encryption
  10. Click OK, the router should restart with the new encrypted settings
  11. Edit the Advanced IP of the host workstation
  12. Recheck enable encryption and reenter the default/chosen encrypted port
  13. Reenter the chosen encrypted password
  14. Click Ok to confirm settings
  15. Shutdown I/NET and I/O server then restart I/NET
  16. Modify the active IO configuration, go to NP routers
  17. All routers should appear on the list now, the existing encrypted routers on the network and the new encrypted router on the network
Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 6047
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore