Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Procedure for correcting duplicate LON device node numbers in a Niagara R2 UNC station

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Procedure for correcting duplicate LON device node numbers in a Niagara R2 UNC station
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa119747
    sesa119747
  • sesa116868
    sesa116868
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1316 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Procedure for correcting duplicate LON device node numbers in a Niagara R2 UNC station

Picard Product_Support
‎2018-09-06 02:48 PM

Issue

Procedure for correcting duplicate LON device node numbers in a Niagara R2 UNC station

Environment

Niagara R2 UNC station

Cause

Occasionally, when a LON device has been removed from use at one site and installed at another site, the previously configured LON subnet and node number can be the same as an existing device in the new installation. The problem typically manifests itself when attempting to learn and commission the new controller using the Workplace Pro.

Resolution

Use the following steps to correct the problem.

  1. Open the "Lon Device Manager" from the right-click menu of the LonWorks Service.
  2. Click "Find" to get a list of all the LON controllers under the UNC. An error message will be displayed indicating that a device with a duplicated subnet and node number has been detected.
  3. Right-click on one of the devices that has the duplicate address. If no right-click menu is displayed, right-click on a different device with the same subnet and node number.
  4. From the right-click menu, select "Properties" then select the "General" tab then select the "Engineering" tab.
  5. In the "Node State" pulldown list, select "Unknown".
  6. Change the node number, displayed in the "NodeID" box, to a value that is not currently used.
  7. Click the "Apply" button to save the changes.
  8. Click the "back-arrow" button to return to the Device List screen.
  9. Reselect the device just changed then click the "Commission" button. In the pop-up window that is displayed, verify that the Neuron ID of the device is correct then click the "Apply" button. Wait for the commissioning process to complete.
  10. 10. If additional devices are shown with duplicated node addresses, repeat steps 3 through 9 for each additional pair of duplicate addresses.
Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 3035
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of