Procedure for Splitting Existing Links to DLA architecture

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Procedure for Splitting Existing Links to DLA architecture
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Derrick_Ratliff
    Derrick_Ratliff
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1614 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Procedure for Splitting Existing Links to DLA architecture

Picard Product_Support
‎2018-09-06 02:00 PM

Issue

Procedure for Splitting Existing Links to DLA architecture

Environment

I/NET

Xenta 527

NPR

Cause

As cable degrade over time it is more economical to split a controller LAN into multiple DLA sites that to re-run the wire. This is especially true when dealing with broken underground wire.

Resolution

This is a basic order of operations for how to split a single link. 

Please select Start > All Programs > I/NET > Manual-Technical Reference Guide and review section 1-11 before proceeding. 

  1. Determine a logical location for the split in the controller LAN
  2. Install the Xenta 527 or NPR and ensure that Ethernet communication if available. (DO NOT plug in the Ethernet cable yet)
  3. Back up the I/NET database
  4. Reconfigure the existing router to be a DLA device.  DO NOT use site 0
  5. Configure the new Router to be a DLA device using a different site address than the first router.  You can use the same station address if needed. Plug in the Ethernet cable
  6. At the I/NET workstation verify that each of the devices is online. You may need to restart the I/O server and verify Reference Hosts. 
  7. At the Workstation you should now have to connect to the Link, then to the controller.
  8. In I/NET configuration, click on Host Masks.  Modify the host mask settings for the existing router and note the settings.  Copy theses settings to the new DLA device(s).
  9. Back up the I/NET database
  10. Physically break the Controller LAN and connect one leg to the new Router. You may need to remove or disconnect any segment of wire that now leads to no where.
  11. At the I/NET workstation you should now be able to connect to each site and see controllers populated under it. If you cannot, a common reason is that you have 2 routers connected to the same controller LAN section and no router connected to the other section.
  12. Select Edit>Host Computer>Network Configuration
  13. Notice that the Split Link has been renamed to DLA Link #.  You can change this name in newer revisions of I/NET
  14. Select the link you have split and click Penetrate.
  15. You will see the sites displayed with " * " next to each. Each site will take the Host Name you gave it during configuration.
  16. Click Save All
  17. Penetrate into the highest numbered site. Click Save all and close.  Then work your through each site from highest to lowest number saving all of the controllers under it.
  18. Open a graphics page and test points that are under each of the sites.
  19. In an access system. You can test by adding or removing an individual from a door under each site.
  20. Backup the I/NET Database.

NOTES:

  • You can not have duplicate station addresses under the same link even if they are on different sites. The controllers are addressed LLSS (Link##Station##) no duplicate LLSS address can exist within an I/NET system.
  • The exception to the above is that all Xenta 527 can use the same station address as that address is not visible from the Host workstation. Each 527 must have a unique link and site address.
Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 4839
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore