Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Problems upgrading/installing SQL server. The SQL Server System Configuration Checker cannot be executed due to WMI configuration on the machine XXXXXXX Error:2147749896 (0x8004...

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Problems upgrading/installing SQL server. The SQL Server System Configuration Checker cannot be executed due to WMI configu...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa177673
    sesa177673
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2203 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Problems upgrading/installing SQL server. The SQL Server System Configuration Checker cannot be executed due to WMI configuration on the machine XXXXXXX Error:2147749896 (0x8004...

Picard Product_Support
‎2018-09-07 06:53 AM

Issue

Problems upgrading/installing SQL server.

The SQL Server System Configuration Checker cannot be executed due to WMI configuration on the machine XXXXXXX Error:2147749896 (0x80041008).

"Not clustered or the cluster is up and online” check fails.

Note: In the screen shot above the clustering check was passed.

Environment

TAC Vista 5.X.X

SQL Server 2000/2005/2008 all versions; upgrades and new installations.

Cause

The WMI (Windows Management Instrumentation) Control is a tool that enables you to configure WMI settings. Inadequate access permission will mean that the user is unable to access the WMI service.

Resolution

If one of these messages appears or other problems are encountered during installation or upgrading of an SQL server, follow the steps below:

1. Check the WMI settings

  • Go to My Computer – either in the start-menu or go directly to the desktop icon if running windows in classic mode – and right-click on it. Select Manage.
  • In the hierarchical tree in the pane to the left, expand Services and Applications.
  • Locate WMI Control and right-click on it. Select Properties from the context-menu.

If the message “Failed to initialize all required WMI classes” is displayed (see screenshot below) read on…

2. Change/check the DCOM settings

  • Open the start-menu, click on Run and type “dcomcnfg”. The Component Services console should open.
  • Expand Component Services and then expand the Computers folder.
  • Select and right-click on My Computer.
  • Select Properties.
  • In the dialogue window that opens up select the COM Security tab.
  • Under Launch and Activation Permissions select Edit Default.
  • Check under Groups or user names to see if the group Everyone has been added. If not select Add, type in "everyone" and then click on Check names. Once the name is confirmed, click on OK.
  • Ensure that the permissions Local Launch, Local Activation and Remote Activation are allowed for the group Everyone.
  • Repeat the above steps for Launch and Activation Permissions but select Edit Limits.

 

  • Click on OK again to close the My Computer Properties window and then close Component Services.

 

 

  • 3. Recheck the WMI Settings
  •  

     

     

    • Go back to the Computer Management console described earlier and locate WMI control under Services and Applications. Right-click on it and select properties.
    • If all the steps have been followed the message should read "Successfully connected to local computer." After this it should be possible to upgrade/install SQL server.

    Labels (1)
    Labels:
    • TAC Vista
    Tags (1)
    • Find more articles tagged with:
    • 4747
    Was this article helpful? Yes No
    No ratings

    Link copied. Please paste this link to share this article on your social media post.

    You’ve reached the end of your document

    WHAT’S NEXT?

    Ask our Experts

    Didn't find what you are looking for? Ask our experts!

    My Dashboard

    Check out the new Feeds and activities that are relevant to you.

    To The Top!

    Forums

    • APC UPS Data Center Backup Solutions
    • EcoStruxure IT
    • EcoStruxure Geo SCADA Expert
    • Metering & Power Quality
    • Schneider Electric Wiser

    Knowledge Center

    Events & webinars

    Ideas

    Blogs

    Get Started

    • Ask the Community
    • Community Guidelines
    • Community User Guide
    • How-To & Best Practice
    • Experts Leaderboard
    • Contact Support

      Ask our Experts

      Have a question related to our products, solutions or services? Get quick support on community Forums

      Email Us

      For Community platform-related support, please email us

    Brand-Logo
    Subscribing is a smart move!
    You can subscribe to this board after you log in or create your free account.
    Forum-Icon

    Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

    Register today for FREE

    Register Now

    Already have an account? Login

    Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

    Welcome!

    Welcome to your new personalized space.

    of

    Explore