Problems installing Webstation 5.1.4 on PCs running Internet Information Services (IIS) 7 or higher.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Problems installing Webstation 5.1.4 on PCs running Internet Information Services (IIS) 7 or higher.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa177673
    sesa177673
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1187 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Problems installing Webstation 5.1.4 on PCs running Internet Information Services (IIS) 7 or higher.

Picard Product_Support
‎2018-09-07 06:57 AM

Issue

Problems installing Webstation 5.1.4 on PCs running Internet Information Services (IIS) 7 or higher. The installation appears to be OK but just before it finishes it "rolls back" to the beginning and webapps is not installed.

  • Installation problems - Webstation 5.1.4 on Windows 2008 server
  • Installation problems - Webstation 5.1.4 on Windows 7
  • Vista 5.1.4 webapps software crashing during install

Environment

Windows 2008 server

Windows 7 (not officially supported)

Vista webapps (webstation)

Cause

This issue is caused due to compatibility issues with IIS 7. Vista 5.1.5 is compatible with IIS 7. Vista 5.1.4. is not compatible with IIS 7.

Resolution

In order to install TAC Vista Webstation successfully on Windows Server 2008 it has to be done in the following order:

Note : Make sure all installation is done as an administrator (Right click the file/application and select "Run as administrator")!

1. Install IIS 7 with IIS 6 Management Compatibility

  • Start the Server Manager (Right-click on Computer in the start-menu or the Computer desktop icon if running classic start-menu and select Manage).
  • Right-click Roles and click Add roles.
  • In the dialogue that opens up click Next and then select Web Server (IIS).

  • In the dialogue that follows click Add Required Features.

  • Click Next (twice).
  • On the select Role services page select ASP.net.

  • In the dialogue window that appears click Add Required Role Services.
  • Click on "Add roles" and then "next" in the dialogue window that opens. Scroll down to "IIS 6 Management Compatibility", check the box and follow the rest of the installation wizard.

2. Install TAC Vista Server

3. As administrator, Run the ASP.NET IIS Registration Tool (Aspnet_regiis.exe) for ASP.NET version 2.0

  • Run the command prompt as administrator and type in the following:
  • %SystemRoot%\Microsoft.NET\Framework\v2.0.50727\aspnet_regiis.exe -i

4. Install TAC Vista Webstation

5. As administrator, Migrate the ASP.NET application configuration to IIS7

  • Run the command prompt as administrator and type in the following:
  • %SystemRoot%\System32\inetsrv\appcmd migrate config "Default Web Site/"

6. Change the Application Pool in IIS7

  • Go to the Webstation/ScreenMate settings in IIS.
  • Select "Advanced settings" under "Manage Application".
  • Change Application Pool" from "DefaultAppPool" to "Classic .NET AppPool".

7. Change the application pool identity

  • Locate the Application Pools in IIS
  • Locate the "Classic .NET AppPool" application Pool
  • Right-click on it and select "Advanced settings".
  • Locate the Identity attribute and set it to "Local System".

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 4745
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of