Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Problems encountered when changing Data Types(Elec Type) with Bacnet Points and using programs to perform COV's on those points

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Problems encountered when changing Data Types(Elec Type) with Bacnet Points and using programs to perform COV's on those poin...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa119747
    sesa119747
  • Carl_Slack
    Carl_Slack
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1628 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Problems encountered when changing Data Types(Elec Type) with Bacnet Points and using programs to perform COV's on those points

Picard Product_Support
‎2018-09-06 02:54 PM

Issue

Problems encountered when changing Data Types(Elec Type) with Bacnet Points and using programs to perform COV's on those points

Environment

  • bCX Controller
  • CyberStation

Cause

Data type (elec type) is changed without sending to the bacnet side will create issue.

Resolution

Changing the Data Type (Elec Type) of a point on the fly can cause issues. Once a point is created on the infinity side and sent to the data base on the bacnet side and a point is referenced from one or the other and a data type (elec type) is changed without sending to the bacnet side can cause issues. One of the issues is that data could quit updating.

Another issue and one that is more noticeable is that if a COV subscription is created from one of the points through a program, the program could disable for one and or the data would not be correct or updated. To get an understanding of what goes on under the hood. Lets create a scenario that is a typical setup to see what is really going on.
-------------------------------
I have a BCX with a B3 controller and have a point in the bcx named bcxPoint (binary data type).
I have a point in the B3 named localPoint(binary data type) and a program named MirrorPrg.
localPoint = myNet\MyBCX\bcxPoint

Save this program and send to database on the bacnet side.

Open the bcxPoint on the infinity side... change the value from 1 to 0 and back and forth while watching the value update
on the bacnet side's localPoint. All is well and works as expected.
Now change the data type on the bcxPoint to Analog and apply. Change the point form 1 to 0 and back and forth, notice that the point on the B3 localPoint on the bacnet side is not updating. But check the program and it is still running.(But not working) Depending if you have other points in a program that sent a COV notification your program can disable. But for our test, we'll force a COV subscription by adding a blank line to the program and saving, notice the program disables. NOTE: the program will appear to still to be running until a COV notification is sent.

This caveat if you think about it makes sense. We subscribe to a COV list, but one of the data types changes without being sent to the bacnet side. On a larger scale lets say you have multiple points in the mirrorPrg and the program disables, not good. In order to correct the issue we described above, we can set the BCX's bcxPoint back to a binary type and perform a send to database on the bacnet side. Open up the program and add a line and then save which recompiles and puts out a new COV subscription.

Don't forget to enable the program.

The above is a workaround in case you get into trouble. But if you have many points you have changed, I would suggest deleting the controller from the bacnet side and then reloading the controller and the performing a find new bacnet devices. This will ensure that you have all data types straightened out. But to be on the safe side, if you are going to be changing data types of points, I would suggest deleting the point on the infinity side and perform a send to database on the bacnet side. This will get rid of all instances of the point. Then create the point with the correct data type and perform a send to database on the bacnet side and make sure you check all programs referencing the point.

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 2782
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore