Printing an Alarm View with hidden columns from Vista Workstation does not give expected results.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Printing an Alarm View with hidden columns from Vista Workstation does not give expected results.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa115370
    sesa115370
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1121 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Printing an Alarm View with hidden columns from Vista Workstation does not give expected results.

Picard Product_Support
‎2018-09-06 12:32 PM

Issue

When columns are hidden in the Alarm View and the view is printed, the column headers are printed correctly but column data is printed as if no columns are hidden.  Therefore, column headers following a hidden column are printed with the wrong data beneath them.

Environment

Vista 5.1.3

Vista 5.1.4

Vista 5.1.5

Vista 5.1.6

Vista 5.1.7

Workstation

Cause

The Alarm View in Vista Workstation can be customised to hide selected columns (right-click in Alarm View and select 'Customize...').  The Customization dialog shows a list of the nine available columns, all selected by default.  Columns can be hidden by deselecting their checkbox, and the display order can be changed by moving columns up or down the list.

On screen, this has the desired result.  However, when the customized Alarm View is printed (right-click in Alarm View and select 'Print'), the results are very different.

For example, the full alarm list contains these columns:-

State     Count     Priority     Last Change     Object ID     Text     Linked Object     Tripped     User

Now hide every column except:  State     Count     Priority     Object ID     Text

The on-screen results are as expected:

State             Count             Priority             Object ID           Text

StateData    CountData     PriorityData    ObjectIDdata    TextData

 

When the Alarm View is printed, this is the result:

State             Count             Priority             Object ID                  Text

StateData    CountData     PriorityData    LastChangedata    ObjectIDdata

 

The column headers are printed correctly, but the column data are printed as if the 'Last Change' column is not hidden., although the correct number of columns is printed.

Reordering the columns using the 'Move Up' and 'Move Down' buttons does not help.  The column data are always printed in the default column order.

Resolution

Only hide columns at the end of the default column list.  Hidden columns in the middle of displayed columns will cause the printout to be incorrect.

This error has been around since Vista 5.1.3  up to the current version 5.1.7.  It may be fixed in a future version.

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 7567
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of