Pinpoint Object not Found error
  • Pinpoint Object not Found error
  • AbeMeran
    AbeMeran
‎2018-09-06 03:16 PM
When browsing for an object to attach to a control in the Graphics the object is seen in the Browse window yet when the object is selected the system generates the error 'Object Not Found'
CyberStation
PinPoint
There is a 'space' or other non alpha numeric character in the name of one of the objects that form the full path to the object being selected.
The offending character can be in the Network name, Main Controller name, Field controller name or the name of the object itself.
The exact root cause of this problem is under investigation as the space character is valid in Continuum object names.
In databases that have exhibited this problem the solution has been to remove the space (or other offending character) from the name.
It has also been noticed that once the problem is fixed the original name can be restored to the object and the problem does not come back.