Pin configuration of the RJ10 for TAC Xenta OP
TAC Vista
Xenta OP
The Xenta OP has two connection methods, the 4 pin terminal blocks and an RJ10 port.
Some users may have the need for making custom RJ10 cables.
The pin order for the RJ10 port is the exact same as the order on the terminal block right next to it. From right to left they are:
  1. C1 (comms 1)
  2. C2 (comms 2)
  3. G+ (24 VAC power)
  4. G0 (24 VAC ground)