Permanently set the filter to only display alarms with a priority of 1-8 in Vista Workstation 4.5
  • Permanently set the filter to only display alarms with a priority of 1-8 in Vista Workstation 4.5
  • sesa150555
    sesa150555
‎2018-09-06 03:01 PM
Trying to filter alarms on Vista Workstation 4.5.
Is there a way to permanently set the filter to only display alarms with a priority of 1-8?
Permanently setting alarm filters allow for creation of custom alarm views.
In Vista 4.5 you can create user profiles, and assign a custom alarm view to the profile.
For more information on how to set up user profiles and alarm viewers see the "TAC Vista IV, Administrating TAC Vista Workstation" manual. If no profile is specified for a user it will use the global object $UserProfile which uses the global object $AlarmView. If you make changes to those objects it will affect all users that are not using their own profiles.