PWM Transducers and I/NET ASCs
  • PWM Transducers and I/NET ASCs
  • Tom_Poovey
    Tom_Poovey
‎2018-09-06 12:54 PM
The PWM Transducer is responding as though it is receiving a continuous signal from I/NET ASC
  • I/NET software all versions
  • Any I/NET ASC
The triac device on the ASC does not totally drop the voltage to zero (0V), thus the PWM input never sees a pulse.
Install a 0.47µF capacitor between the input and ground terminals of the PWM transducer. It will take the bleed voltage to zero and the transducer will see a pulse value.
  • TAC INET
  • 6904