Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PWM Output Configuration in TAC Xenta 121/122 Devices

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • PWM Output Configuration in TAC Xenta 121/122 Devices
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • PeterEdvik
    PeterEdvik
  • MikaelKrantz
    MikaelKrantz

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1777 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

PWM Output Configuration in TAC Xenta 121/122 Devices

MikaelKrantz Champion
‎2019-05-16 06:41 AM

Last Updated: CraigEl Champion ‎2025-11-02 05:51 PM

Issue

How to configure PWM (Pulse Width Modulation) output in ZBuilder for TAC Xenta 121/122 devices.

Product Line

TAC Vista

Environment

  • Xenta 121
  • Xenta 122
  • ZBuilder

Cause

Proper setup of PWM output requires understanding each parameter in the ZBuilder settings window.

Resolution

PWM Cooling2.jpg

 

  1. Activate at % TL
    The PWM output control starts when Terminal Load reaches this value.
  2. Fully active at % TL
    The PWM output control is fully active when Terminal Load reaches this value.
  3. Min control signal %
    The PWM output will not send out lower percentage of full stroke.
  4. Max control signal %
    The PWM output output will not send out higher percentage of full stroke.
  5. Period seconds
    The time for one full PWM period. This period will be cyclically repeated.
  6. Pulse change if change ≥ %
    Applicable only for actuators giving a position directly proportional to the pulse width and not dependent of cyclic updates (PWM with US terminology). This means the output will only activate when the Terminal Load has changed more than the set value, since last activation.
  7. Normally closed
    The TRIAC output is connected to ground (activated) when Terminal Load is zero, and the PWM output is not active. When the PWM output activates, the TRIAC output will not be connected to ground.
  8. Normally open
    The TRIAC output is open, not connected to ground, when Terminal Load is zero, and the PWM output is not active. When the PWM output activates, the TRIAC output will be connected to ground.
Labels (1)
Labels:
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • MikaelKrantz19
  • MikaelKrantz25
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore