PE Program for Announcing Access by VIP to a Door

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • PE Program for Announcing Access by VIP to a Door
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • AbeMeran
    AbeMeran

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1007 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

PE Program for Announcing Access by VIP to a Door

Captain AbeMeran Captain
‎2021-12-08 12:08 PM

on ‎2021-12-08 12:08 PM

Issue

Guidance is needed for creating a PE program for announcing access by VIP to a door

Product Line

Andover Continuum

Environment

  • Continuum Cyberstation
  • Continuum Net Controller II
  • Continuum ACX 2 Controller
  • Continuum ACX 4 Controller

Cause

Need a way to identify a sub-set of credential holders, (Personnel Objects), with access to the site and take some action when one of those individuals gain access to a door.

Resolution

The subset of credential holders is defined via the Department Code which is an attribute of the personnel object.

 

PERSONNEL CONFIGURATION

PersDeptCode.PNG

 

Any person with a Department Code of 600 will be identified as VIP by the PE Program.

 

DOOR CONFIGURATION

 The door(s) need to be configured with a department point (InfinityNumeric) 

*** In this example we are only doing the entry side of the door, the program can be easily modified to handle the exit side of a door as well.

DoorDeptCode.jpg

Upon valid access, Continuum will automatically place the department code from the personnel object in the value of the InfinityNumeric configured at the door for department point.

 

INFINITY PROGRAM CONFIGURATION (Program resides at the controller)

 ***In this example an alarm is sent when VIP enters a door, program/configuration can be easily modified to take other actions such as sending email, sounding an audible alarm, etc.

VIP_ALM_PROG.PNG

 

Here is the code for the InfinityProgram 

'This program monitors the Front Lobby door for access by VIP individuals
'an alarm is dispatched upon door access by VIPs
'Program is LOOPING/AUTOSTART

Object theDOOR
Numeric theCODE
Object theDepPOINT

Line INIT
  theDOOR = MainLobby 'PUT THE FULL PATH TO THE DOOR TO MONITOR HERE
  theDepPOINT = theDOOR LastDepEntrdPnt
  theCODE = 600 'PUT THE DEPT CODE THAT DENOTES VIP HERE

  Goto MONITOR

Line MONITOR
  VIP_Flag = False
  If theDOOR ValidAccess then
    If theDepPOINT Value = theCODE then Goto SendALM
  Endif

Line SendALM
  VIP_Flag = True
  Goto MONITOR

Line E
  If TS > 0 then Goto INIT
Labels (1)
Labels:
  • Andover Continuum
Tags (6)
  • Find more articles tagged with:
  • AbeMeran21
  • access
  • door
  • person
  • subset
  • vip
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore