PCT2 is unreachable using IP 192.168.10.2, with messages similar to:
  • 504 Gateway Timeout
  • Server error - server 192.168.10.2 is unreachable at this moment.
Project Configuration Tool (PCT) 2
The Hyper-V Virtual Ethernet Adapter in Windows, labeled vEthernet (SwitchPctInternal), is not configured with the proper static IP address.
It may be incorrectly configured as DHCP
IncorrectDHCP.jpgor with an incorrect static IP address
  1. Open Properties for vEthernet (SwitchPctInternal)
    • Go to the Networking tab.
    • Select Internet Protocol Version 4 (TCP/IPv4) and click Properties.
  2. Configure the IP Address:
    • Select Use the following IP Address.
    • Ensure the IP address is set to 192.168.10.1.
    • Set the subnet mask to 255.255.255.0.
      Leave the gateway field blank.
Additional Notes
  • Ensure that no other network adapters are conflicting with the vEthernet (SwitchPctInternal) settings.