PCT Project Backup Procedure

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • PCT Project Backup Procedure
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
5482 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

PCT Project Backup Procedure

Admiral StephenYang Admiral
‎2019-08-21 08:25 AM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:35 AM

Issue

Need to backup or share the project with another user.

Product Line

EcoStruxure Building Operation

Environment

Building Operation Project Configuration Tool (PCT) 

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.

Cause

One way of sharing a project is to move it and another way is to Export the project.

Resolution

Move the project

  1. Stop all servers in each project and stop all projects.
  2. Close PCT application.
  3. Copy the “projects” folder from the PCT storage location and paste it to another storage location (suggested by WebHelp topic Move a Project) OR backup all servers through Workstation.

Default PCT Project Folder Locations

  • Versions prior to PCT 1.2
    C:\ProgramData\Schneider Electric StruxureWare\Building Operation\Project Configuration Tool\storagemodule\projects
  • PCT 1.2 or higher
    C:\ProgramData\Schneider Electric EcoStruxure\Building Operation\Project Configuration Tool\storagemodule\projects

Default PCT Template Folder Locations

  • Versions prior to PCT 1.2
    C:\ProgramData\Schneider Electric StruxureWare\Building Operation\Project Configuration Tool\templates
  • PCT 1.2 or higher
    C:\ProgramData\Schneider Electric EcoStruxure\Building Operation\Project Configuration Tool\templates

 

Export the project

In Project Configuration Tool, in the Project view, select the project you want to export.

  1. On the Header toolbar, click the Export project button or right-click on the project and select "Export".
  2. On the Export selected project(s) dialog box, in the Folder box, browse to the folder on your hard drive where you want to save the exported project.
  3. Click OK.
    TIP: You can select multiple projects and export all of them at once.

Note: In order to be more future proof, there is a new export/import format of PCT projects starting in PCT v1.3.2 with exports having an extension of '.pct_export'.  Projects exported at an earlier version have an extension of '.ppb' and they must be converted to '.pct_export' files before import into PCT v1.3.2.    Please refer to point 2.1 in the release notes.

 

Also prior to PCT v1.3.2 the project had to be stopped before export was possible.  In PCT v1.3.2 the project has to be running before it can be exported.

 
 
Labels (2)
Labels:
  • EcoStruxure Building Operation
  • Project Configuration Tool
Tags (3)
  • Find more articles tagged with:
  • JonasBrissman22
  • StephenYang19
  • StephenYang23
Was this article helpful? Yes No
100% helpful (7/7)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore