PCC10 / PCLTA20 Lon Talk adapter configuration for WorkPlace Tech
  • PCC10 / PCLTA20 Lon Talk adapter configuration for WorkPlace Tech
  • sesa116868
    sesa116868
‎2018-09-06 10:52 AM
What application type is required to allow a PCC10/PCLTA20  LonTalk adapter to be used with WorkPlace Tech?
WorkPlace Tech Tool software
Echelon LonTalk adapter (PCC10 / PCLTA20)
This information does not apply to the USB U10 Echelon LonTalk adapter
Selection of the incorrect LonTalk driver application will result in the inability of the WorkPlace Tech software to access the connected LON network.
Change the NI application of the LonTalk adapter
  1. Open the Windows Control Panel
  2. Select the LonWorks Plug N' Play.
  3. Change the NI Application
    1. For a PCC-10 LTA select NSIPCC
    2. For a PCLTA-20 LTA select NSIPCLTA
  4. Click Apply
  5. Click OK to exit the program.
  • TAC IA Series
  • 11838