Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Overall Tap Configuration

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Overall Tap Configuration
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1254 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Overall Tap Configuration

Picard Product_Support
‎2018-09-07 12:47 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:53 AM

Issue

Overall Tap Configuration

Environment

I/NET Seven Site

Cause

Need information on Tap Configuration

Resolution

When you update parameters in a Tap, the changes will take effect when you disconnect from the Tap. If the changes are made to a shared dial Tap, the changes will take effect when the last connected host disconnects from the Tap.

Use the following steps to configure a Tap. Refer to TCON300, I/NET Seven Technical Reference Guide, for a description of Tap configuration parameters.

  1. Select Edit Tap Host (or Link, or LAN) from the main menu. The system displays the Host Tap Configuration editor.
    The Link Tap and LAN Tap configuration editors are similar. This procedure describes the differences.
  2. Assign a Tap Name to the Host, Link, or LAN tap (up to 16 characters).
  3. On site Taps, use the spindial to choose a LAN Address (0 to 63) to identify the tap address on the controller LAN. The LAN Address field applies only to site taps.
  4. Depending on the type of tap, do one of the following:
    • On host and LAN taps use the spindial to choose a LAN Speed.
    • On link taps use the spindial to choose a Speed.
    • On dial taps choose a Tap speaker setting from the drop-down list (Off, Auto, or On).
  5. Use the Firmware Status parameters for information purposes only. These parameters show the current revision number and revision date. These fields are display only, you cannot edit them.
  6. Use the Distribution Parameters fields to specify distribution group number, message priority, and the message mask.
    Note: When utilizing dual Tap functions (site Tap and LAN Tap) in a 7716, 7718, 7728, or 7793 (configured as -03 or -06), the values entered under "Distribution Parameters" in one Tap editor are used by all Tap editors emulated within the same DCU. Only one set of "Control Parameters" have been provided in each DCU.
    1. Select the Distribution Group number (1–4) to match the distribution group of the host PCs to which you want the Tap to send messages.
    2. Set the Message Mask to match the mask(s) of the host PCs to which you want the Tap to send messages.
    3. Set the Message Priority to None, Routine, Priority, or Critical.
  7. The Percent Full field is for AD/AA LAN Taps only. It specifies the number of messages that will be stored in the LAN/Site Tap’s RAM, as a percent of the total available memory, before the Tap calls the host PC. This is a deferred dialing parameter for "Priority" alarms.
  8. The Time Interval field is for AD/AA LAN Taps only.
    It specifies the time interval that must transpire following a "priority" alarm before the LAN/Site Tap calls the host PC. This is a deferred dialing parameter for "Priority" alarms.
Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 1877
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore