Outside sensor not working on a DC1100 or DC1400
  • Outside sensor not working on a DC1100 or DC1400
  • sesa139513
    sesa139513
  • DavidChild
    DavidChild
‎2018-09-06 10:00 AM
DC1100
DC1400
All wiring and terminations have been checked but the outside air sensor is not working.
On the DC1100 and DC1400, the outside air sensor can be shared between a maximum of 3 controllers.
The switch on the rear must be in the up position on one of the controllers.
If there is only one controller fitted, the switch on the rear must be in the up position.