Output does not assume value set by a PE InfinityProgram.
  • Output does not assume value set by a PE InfinityProgram.
  • AbeMeran
    AbeMeran
‎2018-09-06 02:10 PM
An InfinityProgram is setting an output point but the point does not change value, the program is enabled and running.
  • CyberStation
  • CX9900
  • CX9680
  • ACX57xx
  • All infinet and i2 devices
This issue may be caused by a number of reasons:
  1. The InfinityOutput object is disabled.
  2. The InfinityOutput object is manually overridden.
  3. A second program that executes later in the firing order is setting the output object.
  1. Enable the InfinityOutput object.
  2. Return the output override switch to the 'Auto' position.
  3. Solve the contention between programs.
  • 4523