Orion Stack Setup - Loytec NIC852 LNS Communications

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Orion Stack Setup - Loytec NIC852 LNS Communications
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Jonas_Brissman
    Jonas_Brissman
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2214 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Orion Stack Setup - Loytec NIC852 LNS Communications

Picard Product_Support
‎2018-09-10 03:26 AM

Last Updated: Administrator CraigEl Administrator ‎2025-08-28 10:45 PM

Issue

Step-by-step instructions for installing and configuring a Loytec NIC852 dongle (Orion Stack) for enhanced LNS communications.

Product Line

TAC Vista

Environment

Vista Server

Cause

A single Vista server typically supports up to four average-sized LNS networks. Larger networks or multiple LNS ports on one server can degrade communication reliability. The Orion Stack modifies how Vista communicates with the LNS Server, allowing support for up to 28 LNS Ports.

Resolution

Pre-Installation Notes

  • If LonWorks Interfaces were previously configured as your Network Interface, delete the computer’s IP address from the IP-852 tab before proceeding.

Installation Steps

  1. Insert the NIC852 Dongle into a USB slot on the Front-End computer.

    • Ensure the dongle remains plugged in at all times for Orion Stack functionality.

  2. Install Required Software using the Loytec CD:

    • Hardware drivers

    • LConfig interface

  3. Update Drivers

    • Download the latest NIC interface drivers from:
      Loytec Driver Downloads

  4. Verify Installation
    • The Loytec symbol should appear in the Windows system tray.

    • Right-click the icon and launch LConfig.

NIC852 Configuration via LConfig

  1. In LConfig, go to the NIC852 tab:

    • Enable the device

    • Set Transceiver to IP-10L

    • Select the number of LNS Applications (LNS databases)

  2. Click CNIP Configuration:

    • Enter IP addresses for:

      • Device (Front-End Computer)

      • Configuration Server

    • Enter the Device Name (Computer Name)

    • Click OK twice to apply settings

    • Test the configuration before closing

Vista & LonMaker Setup

  1. Open LonMaker:

    • Open the first drawing directory with “Show all network options dialogs” checked

    • Configure the Network Interface:
      • Check “Network Attached”
      • Select the first NIC_852 entry
      • Proceed through dialogs by clicking “Next”
      • Save and exit
  2. To configure each LNS network interface:

    • Go to LonMaker > Network Properties in Visio

    • Use the Network Interface tab to select the correct NIC

 

TAC Network Communication Port Setup

  1. Open TAC Vista System Plug-In:

    • Navigate to LonMaker > System Plug-In > TAC Vista System Plug-In

    • Right-click the Network (top of controller tree)

    • Click Settings

    • Under the Network tab, select Communication Port – Loytec
    • Click OK
    • Update the TAC Network
  2. Repeat Steps 6–10 for each LNS database:

    • Use a different Network Interface for each

Final Notes

  • Once all NICs are configured, the Orion Stack setup is complete.
  • Tip: Add a note on the site’s main graphics page indicating that an Orion Stack is installed. This helps inform remote support engineers and other users.
Labels (1)
Labels:
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 6232
  • JonasBrissman25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore