Operating Systems and SQL Supported in I/NET Seven 2.40, 2.40A, and 2.41

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Operating Systems and SQL Supported in I/NET Seven 2.40, 2.40A, and 2.41
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Tom_Poovey
    Tom_Poovey
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1915 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Operating Systems and SQL Supported in I/NET Seven 2.40, 2.40A, and 2.41

Picard Product_Support
‎2018-09-11 11:29 AM

Issue

Operating Systems and SQL Supported in I/NET Seven 2.40, 2.40A, and 2.41

Environment

  • Windows Server 2003 w/ SP1
  • Windows XP Professional w/ SP3
  • Windows Vista Enterprise w/ SP1
  • Windows 7 Professional 32-bit
  • SQL Server 2000 Desktop Engine(MSDE 2000) SP4
  • SQL Server 2000 Standard
  • SQL Server 2000 Enterprise
  • SQL Server 2005 Express SP3
  • SQL Server 2005 Standard SP3
  • SQL Server 2005 Enterprise SP3
  • SQL Server 2008 Express (32-bit)
  • SQL Server 2008 Standard (32-bit)

Cause

Issues may arrive if the I/NET software and SQL Server versions do not follow the below guidelines.

Resolution

 Click here to download this document in PDF format.

    Operating Systems
    Windows Server 2003 w/ SP1  Windows XP Professional w/ SP3  Windows Vista Enterprise w/ SP1  Windows 7 Professional 32-bit 
SQL Server  SQL Server 2000 Desktop Engine (MSDE2000) SP4   Yes   Yes     
 SQL Server 2000 Standard   Yes       
 SQL Server 2000 Enterprise   Yes       
 SQL Server 2005 Express SP3   Yes   Yes   Yes   Yes 
 SQL Server 2005 Standard SP3   Yes   Yes   Yes   Yes 
 SQL Server 2005 Enterprise SP3   Yes       
 SQL Server 2008 Express (32-bit)         Yes 
 SQL Server 2008 Standard (32-bit)         Yes 

General Notes:

  1. Do not mix versions of SQL server among equalized or client/server workstations in your TAC I/NET Seven system. Ensure that the edition of SQL server installed on each workstation used in a client/server or equalized setting are based on the same version of Microsoft SQL, either 2000, 2005, or 2008.
  2. It is strongly recommended that you defragment the PC's hard drives on a regular basis. Severely fragmented hard drives can cause poor system performance and in some cases can introduce data errors.
  3. The use of Microsoft SQL Server 2005 Standard or Enterprise edition, or any edition of Microsoft SQL Server 2008 will require that the PC have at least 2 GB of RAM.
  4. Microsoft SQL Server 2005/2008 Express Edition cannot be used on a TAC I/NET Seven filemaster.
Labels (1)
Labels:
  • TAC INET
Attachments
Tags (2)
  • Find more articles tagged with:
  • 5354
  • inet
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore